Wanted to share a recent experience that I had in troubleshooting ratchet mechanism of our 20 MW frame V Gas Turbine
Problems :
1. Jaw clutch failed to engage.
2. Forward stroke not achieved.
Observations :
1. Ratchet pump motor pressure was found to be 64 bar
2. No pressure in FS port of ratchet mechanism.
3. Low pressure in VM2 inlet.
Troubleshooting steps taken :
1. VR2 setting checked and was found to be at 70 bar.
2. FH1 filter cleaned and reinstalled
3. FH5 filter cleaned and reinstalled
4. 2.3 mm dia orifice cleaned and reinstalled
5. Operation of 20 CS was checked by forcing it from Control system and tested using the test point in the SOV. The test point went inside and got stuck when 125 DC was supplied and was released on cutting the supply off.
These steps didn't resolve the issue.
6. Further self sequencing valve was replaced. It was of no help.
7. 33 HR operation was checked and found OK.
8. 33 CSE was also checked and found OK.
Even after the above steps no improvement was found in the oil pressure to VM2 and FS. However, pressure was found to be around 64 bar after FH1 and the inlet tube to 20 CS got heated up with the ratchet pump motor in operation.
*20 CS was dismounted and it's operation was checked. The plunger inside the valve didn't move on applying 125 DC from the control system but the test point was energised and no ground fault was detected in the control system.
*20 CS was energised by providing external 125 VDC, the plunger now moved. Negative leg was found to be faulty and was replaced with a different negative leg.
*20 CS was remounted and ratchet pump motor was re-started.
**Jaw clutch got engaged and forward stroke achieved.
Problems :
1. Jaw clutch failed to engage.
2. Forward stroke not achieved.
Observations :
1. Ratchet pump motor pressure was found to be 64 bar
2. No pressure in FS port of ratchet mechanism.
3. Low pressure in VM2 inlet.
Troubleshooting steps taken :
1. VR2 setting checked and was found to be at 70 bar.
2. FH1 filter cleaned and reinstalled
3. FH5 filter cleaned and reinstalled
4. 2.3 mm dia orifice cleaned and reinstalled
5. Operation of 20 CS was checked by forcing it from Control system and tested using the test point in the SOV. The test point went inside and got stuck when 125 DC was supplied and was released on cutting the supply off.
These steps didn't resolve the issue.
6. Further self sequencing valve was replaced. It was of no help.
7. 33 HR operation was checked and found OK.
8. 33 CSE was also checked and found OK.
Even after the above steps no improvement was found in the oil pressure to VM2 and FS. However, pressure was found to be around 64 bar after FH1 and the inlet tube to 20 CS got heated up with the ratchet pump motor in operation.
*20 CS was dismounted and it's operation was checked. The plunger inside the valve didn't move on applying 125 DC from the control system but the test point was energised and no ground fault was detected in the control system.
*20 CS was energised by providing external 125 VDC, the plunger now moved. Negative leg was found to be faulty and was replaced with a different negative leg.
*20 CS was remounted and ratchet pump motor was re-started.
**Jaw clutch got engaged and forward stroke achieved.