I was asked by a Client to provide calculations for a typical IS circuit of their project. I found different Hart certified DP transmitter vendors like Yokogawa, Emerson and Invensys stating a minimum of 16.4-17 V at the transmitter terminals in order for Hart to operate (despite of their transmitter can work with 10.5-11 volts without Hart).
However to power the transmitter from an isolator type Safety Barriers from P+F; MTL; (and others Hart certified) a minimum of 15 or 16 volts is provided to power the transmitters. So evidently if both requirements were true they cannot work together in the same circuit which we know that is not the case.
So trying to find the truth I found the Hart Physical Layer specification that in page 50/51 list the power supply requirements for Hart and there is no a single mention to a minimum voltage for Hart to operate.
I called both; IS barrier and TX vendors and none of them wants to change or admit their statement is incorrect so based on what I've learned about Hart I am pretty sure there should be no minimum (at least below 10.5 v) voltage requirement for Hart to operate and I am planning to move on with my calculations discarding this voltage limitation.
Am I correct on this?