homeload of two generators connected to one step-up transformer

Iam asking about the homeload arrangement for two gas turbines connected to one step-up transformer, the type is GE frame 9 and the UATs are connected to 15 Kv and it is after the GCB . The question is what is the configuration of the homeload situation if one or both the units are tripped???
 
The unit which tripped by 52L (Line circuit breaker ) or by 52G (Generator circuit breaker)?

The tripped unit by 52L should feed Unit or sometimes Plant auxiliaries equipments
 
Hello

Thank you for sharing SLD

When one GT IS TRIPPED then 52L TRIPPED/OPENED you should have GT 1 OR 2 OR both supplying UATs ...as you said that Step up Transformer is isolated from grid

But when GTs one or two tripped then 52G should get tripped to depending on the trip cause...

There is 2 differents 6.6KV that should be fed by GT 1 or 2 ..

House load should be ok on this configuration ..

I see that there is black start option ...

I will study in more details that thread and come back with notes



if the unit is tripped by 52L, then the UATs of the units are both de-energized, so how the units are going to homeload
 