Hello,
We have several Frame 9E units. Sometimes we're tripping at Gas-to-Liquid changeover, which we perform once per week or two. Usually, the problem is fuel pipes and other volumes not completely filled with liquid fuel. By slowing rate of changeover from 30 sec to 5-10 times more (reducing FXK1 constant), we always succeeding. But, when we (I&T) not at site and operators not allowed to make a simulation, they are in trouble.
Is there a limitation to prevent a hardware damage for working in Mixed Fuel Mode for not 30 sec but, let's say, 3 min? Can we implement this rate constantly?
Thanks.
We have several Frame 9E units. Sometimes we're tripping at Gas-to-Liquid changeover, which we perform once per week or two. Usually, the problem is fuel pipes and other volumes not completely filled with liquid fuel. By slowing rate of changeover from 30 sec to 5-10 times more (reducing FXK1 constant), we always succeeding. But, when we (I&T) not at site and operators not allowed to make a simulation, they are in trouble.