Connecting Delta SV2 PLC Using Modbus
Connecting PLC Delta SV2 to Multimeter KAEL via ModBus RTU

Hello,

How I can connect PLC Delta SV2 to Multimeter KAEL (MULTIMET-01-PC-96) by using RS-485 ModBus - RTU??

Best Regards ..

The manual here
http://www.kael.com.tr/eng/pdfler/MULTIMET-01-PC%20eng.pdf
states on page 9 that the device can only reply with one variable per Modbus message/transaction using Function Code 03 (read Holding Register).

The RS-485 wiring has Sg (signal ground) driver lines A and B, and a terminal for TR. I suspect TR is terminating resistance, but it connects to the A driver on one slave device only. Who knows?

Furthermore, that document does not have a Modbus slave table of registers/ addresses and the associated units for the data values. I'd want to find that document before I spent one minute on anything else Modbus.

To connect, you need a Modbus Master, because these are slaves.

It appears that the manufacturer offers a software package.
http://www.kael.com.tr/eng/pdfler/MULTIMET-01-PC%20eng.pdf
You might want to see what that software does and whether it meets your needs before struggling through a Modbus implementation.

This link shows ModBus Registration Table <<

http://www.kael.com.tr/eng/pdfler/Multimet-01-PC-96%20register%20table.pdf