a question about intrinsically safe instrument
What happens if we install an intrinsically safe instrument without installing a safety barrier before it?

As we know for any intrinsically safe instrument we should install a safety barrier to limit the energy fed to the instrument.

My question is: what happens if we install an intrinsically safe instrument without installing a safety barrier before it?

Will it operate/run well?

What will be its Ex protection capability in that case?

0 out of 1 members thought this post was helpful...

The barrier is for Fire Safety.

You should know that it is based on the Area Classification for your section of plant.


1 out of 1 members thought this post was helpful...

The instrument will operate and run properly. However, it will no longer be an intrinsically safe installation, it will not meet Ex requirements because in the event of a power supply failure there will be the capability of producing a spark with sufficient energy to ignite an explosive gas.

1 out of 1 members thought this post was helpful...

The purpose of the I/S barrier is to prevent electrical faults (over voltage) in the safe area from getting to the I/S device in the hazardous, where the fault could damage the device and create an arcing-sparking ignition source.

No barrier; no protection from faults on the 'safe' side.

1 out of 1 members thought this post was helpful...

You will find that most modern 2 wire instruments are supplied rated as general purpose NEMA-4, IS and explosion proof.

If you install it without an IS barrier it is only certified for GP service.

Install it is a proper IS loop with correct wiring and an IS barrier and it is rated IS.

Install it with the proper Ex-d rated conduit, fittings and cabling and it is Ex-d.

good luck