Hello to all.
Introduction: The unit is Dual-Fuel 7FA turbine, DLN2.6. Primary Fuel is Natural Gas.The liquid fuel system have 3-way valve and re-circulation system. The unit runs on liquid for testing each outage period. We mainly suffer from two issues related to 3-way valve.
The first is liquid fuel coking inside the 3-way valves which causes high exhaust temperature spreads. The reason we have the spread issue is that in Summer, when the operations see smoke coming from the turbine compartment (indicating there is external liquid fuel leak) they isolate the liquid fuel re-circulation system without purging it with N2. But I believe this doesn't have anything to do with the problem in hand because this problem we suffer from long time.
Second issue we face is that while the unit on turning gear, we force the re-circulation system, and the 3-way valve passes amount of liquid into the Cans where it shouldn't. This is caused by the failure of the seals. Also when you run the unit on liquid. first the turbine will go into purge for some time, during purge time the liquid re circulation will start to get rid of any air in the lines. during this purge time and re circulation ON maybe some liquid will leak into the Cans and go to the false start drain. Although that we have these issue, but I think they are not the cause of the issue I will talk about. Because We have been experiencing these issue since long time but the issue I will share is new one.
As regular, we do borescope for all units during outage. One of the units showed fuel nozzle Carbonization nearly in all Cans. We have GE office for consulting. according to them this is the first time this happens in our Turbines. They have sent the picture for Engineering waiting for their reply. In the meantime, I wanted to share the pictures with you and benefit for the good experience you have, and I am ready for any more details you want me to provide.
I don't remember there was any alarm before this problem occurred
Next week we will do scheduled PMs for the same unit, like changing the liquid fuel filter (I think they don't have high delta P), cleaning the LF Strainer, etc.
The Borescope pictures are in the following links
Note: We have started the re-circulation while the unit on turning gear before doing the Borescope. Since some 3-way valves are passing, you will see liquid at the liquid fuel passage (the hole in the center)
https://drive.google.com/file/d/0B9R-rponHkn5eTN2NnUtM0Z6TDg/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5cVB3QTdfTVJHZ2s/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5dlRSSlcxWkhMbXc/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5cjAwTlRGbkRsamM/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5SGgzcjM4QXQ1ZVU/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5V2RlalhGdlR4TlU/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5dW1EdGhvVkMyWVk/view?usp=sharing
Introduction: The unit is Dual-Fuel 7FA turbine, DLN2.6. Primary Fuel is Natural Gas.The liquid fuel system have 3-way valve and re-circulation system. The unit runs on liquid for testing each outage period. We mainly suffer from two issues related to 3-way valve.
The first is liquid fuel coking inside the 3-way valves which causes high exhaust temperature spreads. The reason we have the spread issue is that in Summer, when the operations see smoke coming from the turbine compartment (indicating there is external liquid fuel leak) they isolate the liquid fuel re-circulation system without purging it with N2. But I believe this doesn't have anything to do with the problem in hand because this problem we suffer from long time.
Second issue we face is that while the unit on turning gear, we force the re-circulation system, and the 3-way valve passes amount of liquid into the Cans where it shouldn't. This is caused by the failure of the seals. Also when you run the unit on liquid. first the turbine will go into purge for some time, during purge time the liquid re circulation will start to get rid of any air in the lines. during this purge time and re circulation ON maybe some liquid will leak into the Cans and go to the false start drain. Although that we have these issue, but I think they are not the cause of the issue I will talk about. Because We have been experiencing these issue since long time but the issue I will share is new one.
As regular, we do borescope for all units during outage. One of the units showed fuel nozzle Carbonization nearly in all Cans. We have GE office for consulting. according to them this is the first time this happens in our Turbines. They have sent the picture for Engineering waiting for their reply. In the meantime, I wanted to share the pictures with you and benefit for the good experience you have, and I am ready for any more details you want me to provide.
I don't remember there was any alarm before this problem occurred
Next week we will do scheduled PMs for the same unit, like changing the liquid fuel filter (I think they don't have high delta P), cleaning the LF Strainer, etc.
The Borescope pictures are in the following links
Note: We have started the re-circulation while the unit on turning gear before doing the Borescope. Since some 3-way valves are passing, you will see liquid at the liquid fuel passage (the hole in the center)
https://drive.google.com/file/d/0B9R-rponHkn5eTN2NnUtM0Z6TDg/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5cVB3QTdfTVJHZ2s/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5dlRSSlcxWkhMbXc/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5cjAwTlRGbkRsamM/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5SGgzcjM4QXQ1ZVU/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5V2RlalhGdlR4TlU/view?usp=sharing
https://drive.google.com/file/d/0B9R-rponHkn5dW1EdGhvVkMyWVk/view?usp=sharing