HI.
We have in our site two turbines MS6000 both running on gas fuel (not DNL), control system MKV TMR <I>. We have noted that with a target of 19 MW (demanding of the grid) both turbines run with 19 MW each of them. CPD:9,21 bar (both), fsr:36,73% / 36,41%, TTXM:375 / 373 ºc, igv:85,8 (both), tnr: 101,96% (Both), respectively.
Now when the target of the grid is for example "Base Load," we note a significant difference in load of both as following:
CPD:9.51 / 9.67 bar, fsr:59.65% / 60.09%, igv:85,3 (both), tnr: 103,82% / 104,03%, respectively. dwatt: 31.9 MW / 33.5MW.
We suspect that difference of load of both turbines is due to the difference in cpd. But why we don't have that difference in cpd when both turbines run in a load below 20 MW. The stroke of the GCV and SRV and IGV are within the values of control spec.
Is it a problem with the compressor discharge?, Do we need a wash compressor?, since we have checked the cpd transmissor and 20 CB and both are ok.
Thank you very much.
We have in our site two turbines MS6000 both running on gas fuel (not DNL), control system MKV TMR <I>. We have noted that with a target of 19 MW (demanding of the grid) both turbines run with 19 MW each of them. CPD:9,21 bar (both), fsr:36,73% / 36,41%, TTXM:375 / 373 ºc, igv:85,8 (both), tnr: 101,96% (Both), respectively.
Now when the target of the grid is for example "Base Load," we note a significant difference in load of both as following:
CPD:9.51 / 9.67 bar, fsr:59.65% / 60.09%, igv:85,3 (both), tnr: 103,82% / 104,03%, respectively. dwatt: 31.9 MW / 33.5MW.
We suspect that difference of load of both turbines is due to the difference in cpd. But why we don't have that difference in cpd when both turbines run in a load below 20 MW. The stroke of the GCV and SRV and IGV are within the values of control spec.
Is it a problem with the compressor discharge?, Do we need a wash compressor?, since we have checked the cpd transmissor and 20 CB and both are ok.
Thank you very much.