Hi All, I am wondering about the proper type of level transmitter for closed drain system.
E Thread Starter Elmira Dec 9, 2016 #1 Hi All, I am wondering about the proper type of level transmitter for closed drain system.
D David_2 Dec 11, 2016 #2 If the tank has a mix of something and water then non-contact radar might avoid the situation described in the report at this link: https://www.norskoljeoggass.no/Glob...ark/Faktaark 2014/Fact sheet 2014-H_Final.pdf The condensate overflowed into the closed drain tank's spill line. The cause was a level measured by DP and incorrect level was based on the density/SG of just water, not on the mix.
If the tank has a mix of something and water then non-contact radar might avoid the situation described in the report at this link: https://www.norskoljeoggass.no/Glob...ark/Faktaark 2014/Fact sheet 2014-H_Final.pdf The condensate overflowed into the closed drain tank's spill line. The cause was a level measured by DP and incorrect level was based on the density/SG of just water, not on the mix.
R RoyMatson Dec 12, 2016 #3 You aren't giving us much to go on. What's in the drain? Can you describe it? Under pressure?